7/22/2015 9:49 AM | |
Posts: 9 Rating: (0) |
Sir, I am using CPU 1214C having MLFCB no. 6ES7 214 - 1AG04-0XB0. Need commissioning support for the following. In the Onboard integrated output Q 0.0 and Q0.1 Is assigned for the Pulse and direction output in the technology objects the function MC-Power, MC-Reset, MC-Jog etc for the third party servo drive. The signal to that device will be via wired. When I executed the Programme using MC-Power ( Servo on enable) and then MC- Jog function to Fwd forced via watch table and the velocity is given. But the problem was there is no response on the drive. kindly advice whether the wiring for the pulse train output and problem execution if any to check the pulse output is alive or not. Application: Pick and place the bearing component using Handling unit. To move left and right movement with different position will work using servo drive ( SMC Electric Servo actuator )and Up and down movement will work using pneumatic cylinder. With best regards, P.Kathirvelu
---------------------------------------------------------------------------------------------------- |
Last edited by: Min_Moderator at: 7/22/2015 10:20:14 AMNew subject after splitting |
|
7/22/2015 10:44 AM | |
Posts: 9 Rating: (0) |
Hi, Please see the attached document for your immediate reference. Note : For servo position control use page no. 10 Regards, kathirlat AttachmentLECSA (simplified) (1).pdf (493 Downloads) |
7/22/2015 12:12 PM | |
Posts: 5225 Rating: (1185) |
By default this drive is NPN. |
7/23/2015 1:45 PM | |
Posts: 9 Rating: (0) |
Hi, Please see here with attached PDF for SMC - LECSA servo Actuator using PTO. Kindly advice... AttachmentLEC2-OM026xxim_OperatingManual.pdf (542 Downloads) |
7/23/2015 1:47 PM | |
Posts: 9 Rating: (0) |
Hi, This is next PDF file continous of the previous one attachement AttachmentLEC1-OM026xxim_OperatingManual.pdf (474 Downloads) |
7/23/2015 1:48 PM | |
Posts: 9 Rating: (0) |
Hi, This also another attachment please.... AttachmentLEC-OM026xxim_OperatingManual.pdf (402 Downloads) |
7/23/2015 1:50 PM | |
Posts: 5225 Rating: (1185) |
An add on card can be an option.. see attachment. AttachmentExtract_S7-1200 System manual.pdf (455 Downloads) |
7/29/2015 11:31 AM | |
Posts: 9 Rating: (0) |
Hi, How i can get Sink PTO in the CPU 1214C module. Pls let me know |
7/29/2015 11:54 AM | |
Joined: 12/16/2012 Last visit: 4/24/2024 Posts: 652 Rating: (130) |
Hi! One solution would be to use high speed optocouplers between the PLC and the drive. E.g. like this one (100kHz): https://www.phoenixcontact.com/online/portal/us?urile=pxc-oc-itemdetail:pid=2902970 Or a converter: (however, this may be too slow for you at 15kHz) https://www.phoenixcontact.com/online/portal/us?uri=pxc-oc-itemdetail:pid=2964319&library=usen&tab=1 P.S. as I mentioned before, if you have fixed positions, you can use a position table in the drive and normal DO at the PLC - then there's no need for PTO and source to sink interface. |