Can be Connected the distributed I/Os via PROFIBUS ET200U to S7-1500? |
2/28/2016 3:38 PM | |
Joined: 9/27/2006 Last visit: 5/30/2023 Posts: 12025 Rating:
|
Hello behrooz; This will depend on the model of head module you are using in your ET 200U station. If you have a 6ES5 318-8MA1x, the your head module is designed for Sinec L2 and recognized as an ET 100U station, an S5 network close to Profibus-DP, but incompatible. If you have either a 6ES5 318-8MB1x or 6ES5 318-8MC1x interface module then you can download the gsd files for each (make sure you select the right category) and use them as ET 200U Profibus-DP slaves in your network:
PROFIBUS GSD files : ET 200U
https://support.industry.siemens.com/cs/ww/en/view/113512 These links will provide some information on the requirements for an ET 200U station:
Coupling ET200U DP (6ES5 318 8MB12) to an S7 master
https://support.industry.siemens.com/cs/ww/en/view/217419
Configurable DP-slaves for IM 308B (do not take into account the comment on COM ET 200 configurator)
https://support.industry.siemens.com/cs/ww/en/view/16503056
Hope this helps, Daniel Chartier |