1500 and S110 at the same PROFINET, at the bus has three S110, two G120C. my problem is :set S110 to IRT ,at compile ,have error . how can i to do ? |
9/4/2015 9:07 AM | |
Posts: 305 Rating: (2) |
.... |
9/4/2015 9:23 AM | |
Joined: 5/12/2006 Last visit: 10/2/2024 Posts: 22388 Rating: (3015) |
Hello, Telegram can't used for IRT Mode, for IRT you must use Telegram 3 /.
Christoph |
9/4/2015 10:15 AM | |
Posts: 305 Rating: (2) |
i change tele3 ,ti is ok. how can i know witch tele by IRT is right ? |
9/4/2015 10:17 AM | |
Posts: 305 Rating: (2) |
i set the S110 at speed mode ,may i control it motion at speed 、torque ? |
9/4/2015 11:23 AM | |
Posts: 305 Rating: (2) |
at detail overview ,it is back for me set the telt ,i want before setting ? does have any idea ? |
9/4/2015 11:37 AM | |
Posts: 305 Rating: (2) |
this is my bus network . please look at it doea have any problem (S110 / G120C by IRT ; HMI / ET200SP by RT) ?at ET200SP and HMI ,i design a SCALANCE XB005 . |