9/13/2019 3:39 PM | |
Joined: 2/10/2010 Last visit: 11/21/2023 Posts: 35 Rating: (0) |
Dear collegues, I try to change network settings of S7-1500 PLC trough it's display. After applying changes there is a message "The IP settings are write-protected". As I know, PLC has no know-how protection, or other passwords. In Settings menu "Protection" there are "No protection level", and "Disallow in RUN". I didn't found come suitable instructions in manual (chapter 13) or that one. |
Last edited by: Jen_Moderator at: 09/16/2019 11:02:58Optimized link. |
|
9/13/2019 3:50 PM | |
Joined: 7/7/2010 Last visit: 9/6/2024 Posts: 15157 Rating: (2415) |
Maybe this setting (see attached image) is not correct?
|
science guy |
|
This contribution was helpful to1 thankful Users |
9/16/2019 8:15 AM | |
Joined: 2/10/2010 Last visit: 11/21/2023 Posts: 35 Rating: (0) |
Yes, that setting is "Set IP address in the project". I'll change it. |