2/7/2018 3:33 PM | |
Posts: 29 Rating:
2/8/2018 9:28 PM | |
Joined: 5/6/2010 Last visit: 9/29/2023 Posts: 1911 Rating:
Hello citizenBar, I think you have a problem with your power wiring of all cards. Here is the link to the manual https://support.industry.siemens.com/cs/de/en/view/86140384 If I see it right then you wire the supply of the cards as follow: CPU L+ to module 1 pin 19 (DO) Please look at the manual page 2670 The best way is you connect all the modules separately I hope this is helpful to solve your problem. regards |
This contribution was helpful to
1 thankful Users |
2/13/2018 8:13 AM | |
Posts: 29 Rating:
I will be very thankfull for safety addressing and for all! :) |