hi, i am using a cpu 315 2PN/DP(6ES7 315 2EH14 0AB0). Iam also using 512kb mmc(6es7-953-8LJ20-0AA0)I tried to communicate using mpi and pc adapter cable.but in setpg/pc , i am getting the message "bus parameter couldnot be determine because of communication error".My cpu is showingSYSTEM fault and not going to run mode.But when i remove mmc there is noSYSTEM faultand it is going to run mode and i am able to communicate via pg/pc. please check the attached screenshot Attachmentcommunication error.zip (110 Downloads) |
Last edited by: murukesh at: 4/27/2011 7:42 AM |
|
4/27/2011 10:23 AM | |
Posts: 3 Rating:
|
It probably comes from the MMC that is unformatted. Try to use S7imgWR.exe and the attachement hereby. (Find it here, for example: http://personal.telefonica.terra.es/web/suwe/) I am using S7imgWR.exe with my internal desktop MMC reader/writer. It will probably solve your problem but of course will also delete ALL existing data of your MMC. AttachmentMMC_empty_512Kb.zip (167 Downloads) |
4/27/2011 10:52 AM | |
Joined: 4/24/2006 Last visit: 3/24/2025 Posts: 8905 Rating:
|
Dear murukesh, Perhaps you can reset to delivery state. Here is a link to manual: SIMATIC S7-300 CPU 31xC and CPU 31x Installation See chapter 9.5 Best regards, Wizard |