Hi leonwang11 you may want take a look on this http://support.automation.siemens.com/WW/view/en/1188622 Hopefully helps |
7/20/2011 9:17 PM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello Leon; The reason it is so easy to communicate with your CompactLogix PLC is because you were using Ethernet/IP, which is a protocol used by Rockwell, with your barcode scanner; Siemens does not support this protocol, so you have to change the way you connect to the barcode. First, you could look for a protocol converter between Rockwell's Ethernet/IP and Siemens' Industrial Ethernet (on the CP 343-1). Siemens has an application note on the use of an Echochange gateway just for this purpose: Communication between SIMATIC S7 and Allen-Bradley ControlLogix CPUs via Ethernet: Use of "Echochange" gateways Or you could use other protocols supported by Sick:you could selecttheir TCP/IP interface, also supported by the CP 343-1; you will have to program all the data exchange strings between the PLC and the scanner; ask Sick for more technical information. Or you could use a Profibus-DP interface between the S7-300 CPU and the barcode reader. This would be the easiest solution fior you, as Profibus-DP is natively supported by most Siemens PLCs.Sick will provide the required module and gsd file, along with the registers available for data exchange. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 7/20/2011 9:27 PMLast edited by: dchartier at: 7/20/2011 9:26 PM |
|
7/21/2011 3:58 AM | |
Joined: 5/1/2011 Last visit: 4/26/2024 Posts: 19 Rating:
|
Hi Marciano: Thanks a lot for your fast reply andhelp. Best Regards Leon |
7/21/2011 4:00 AM | |
Joined: 5/1/2011 Last visit: 4/26/2024 Posts: 19 Rating:
|
Hi Chartier, Thank you very much, you helped me save a lot of time. Best Regards Leon |
8/2/2011 5:14 PM | |
Joined: 5/1/2011 Last visit: 4/26/2024 Posts: 19 Rating:
|
Hello Dcharter, Thanks. Leon |
Follow us on