Hello Subhash Agrawal the one thing that sticks out from your very detailed description is that the CP340's with the most connected devices seem to the worst affected. Due to the number of devices connected to each, they'll most likely also have the longest serial cable runs (this is an assumption) andI wonder if perhaps you pick up some interferencewhich leads to the lock up of the CP340 comms. Worthwhile checking anyhow that teh serial cabel is installed away from motor and power cables and the likes. The other thing to check is how you handle the communication calls. You will (presumably) have at least 14 FB2&3 calls in your logic (one per CP340, I presume that you multiplex eachFB2&3 callper CP 340 to read/write from each device connected to that CP, corrrect?). My question is if you call alleach of the 14 FB2&3 pairs (one FB2&3 pair per CP340) independently of each other and without regards to each? If so, please be aware that FB2 (P_RCV) uses SFB52 (RDREC) and that FB3 (P_SEND) uses SFB53 (WRREC) and that the restrictions from the FAQ below apply (i.e. you will may need to cut the number of simultaneously active FB2&3 callsdown to only 4 for your 315): What restrictions are there for active jobs when communicating with SFC 58 / SFC 59 and SFB 52 / SFB 53 via PROFIBUS DP and PROFINET IO? I hope this helps and please let us know what you find. |