1/4/2012 1:14 PM | |
Joined: 4/22/2010 Last visit: 2/15/2024 Posts: 5697 Rating: (711) |
Hello, In addition to that, the S5 adapter module for the 400 was for some special modules not for normal i/o see: http://support.automation.siemens.com/WW/view/en/42672 For the connector side on the module there are also adapters, : https://a248.e.akamai.net/cache.automation.siemens.com/dnl/zE/zE0NzcyOQAA_27227021_TxtObj/3_Adapter_Eng_V3_0.PDF Regards, Marcjan |
Problem solved? |
|
1/4/2012 1:27 PM | |
Joined: 10/7/2005 Last visit: 3/28/2024 Posts: 3002 Rating: (1045)
|
Hello AjayG if you are not afraid to use some non-Siemens gear and have either 115U or 135/155U I/O racks, you can also convert these to DP Slave I/O station (and as such of course use them with S7-300's) via the IM 306DP Slave module. Note that you will be limited to usage of standard I/O cards in the S5 racks (e.g. you can NOT useFM's, CP's, IP's etc.), but I hope this helps anyhow. |
Cheers |
|