Hello, which Transmission Rate you need. Up to 400m you can use 500 kBit/s, for higher Transmission rate you should use repeater for this distance. Configuring: DP Slave -> Open the properties if the DP Interface of the SLave PLC and set the mode to DP_Slave. Select the PROFIBUS Network from the master and in the Master config insert a i-Slave object from the catalog, here you can configure the Transferareas. https://support.industry.siemens.com/cs/ww/en/view/19449428 https://support.industry.siemens.com/cs/ww/en/view/23847972