4/11/2012 10:29 AM | |
Joined: 8/31/2005 Last visit: 9/14/2023 Posts: 2194 Rating:
|
The older F-DI/F-DO modules only have module wide passivation, with the newer ones you can select module wide or channel selective passivation. The information can be found in the manual for the F-DI module. You gave us the order number of the F-CPU, but we need the order number of the F-DI module to tell you what modes your module supports. Here you can find informations on (de-)passivation: http://support.automation.siemens.com/WW/view/en/22304119 |
|
|
4/16/2012 4:23 PM | |
Joined: 9/27/2005 Last visit: 3/16/2022 Posts: 203 Rating:
|
Hi AGR, take a look: http://support.automation.siemens.com/WW/view/en/23718256 http://support.automation.siemens.com/WW/view/en/23719686 Best Regards Morten |