2/13/2014 3:21 PM | |
Joined: 9/27/2006 Last visit: 9/10/2024 Posts: 12282 Rating: (2682)
|
Hello Yogendra; Hot-swapping of IO modules is designated in the Siemens world as CiR ("Configuration in Runtime"). This should help you find information on the Siemens support websiter (use the search box at the right of this page). The distributed modules you selected will work (see the link below) but not your CPU: only the S7-400 CPUs will support CiR, with restrictions to newer firmware levels: Plant modification during operation via CiR Hardware Requirements You require the following hardware configuration in order to be able to modify the configuration of a system in RUN mode via CiR:
Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
2/14/2014 9:37 AM | |
Joined: 10/7/2005 Last visit: 9/10/2024 Posts: 3020 Rating: (1054)
|
Hello YogendraG Hot Swap (aka Module change during operation) is available for Profibus as well as Profinet ET200M's. For reasons only known to Siemens, you need to do GSD file basedconfiguration for a Profibus ET200M on an S7-300 (and OB83 is not supported either in that case). Have a look at "Module change during operation" - Configuration and system requirements for more on this. With a Profinet ET200M it is a simple tick mark in the ET200M's properties to enable Module change during operation (be it a an S7-300 or 400 as the PN I/O Controller). In either case, make sure you have all the required error OB's in your S7 to avoida CPU stop and the FAQWhich organization blocks do you have to load into the CPU to ensure that the CPU does not go into the "STOP" status when a remote I/O fails? will give you all the details on this. I hope this helps |
Last edited by: fritz at: 2/14/2014 10:03 AMtypos Cheers |
|
This contribution was helpful to3 thankful Users |
9/5/2016 9:50 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
New question published by PriyankaSud is split to a separate thread with the subject Does IM 151-8 standard 6ES 71511AA050AB0 support hot swapping feature?. Best regards |