Joined: 5/12/2006 Last visit: 9/3/2024 Posts: 22352 Rating: (3006) |
Hello, first you should check why the PLC is in STOP Mode. Do you access the Slave during Startup and get a access error ? https://support.industry.siemens.com/cs/it/en/view/98278878
Christoph |
Last edited by: ChristophD at: 9/12/2016 2:08:50 PM |
|
9/12/2016 2:50 PM | |
Posts: 4 Rating: (0) |
Thank you so much! creating an empty OB86 solved the problem. thank you again |