7/21/2014 9:19 AM | |
Posts: 1368 Rating:
|
Hello, if cognex is a PROFINET device,there must be a GSD file for this. http://www.cognex.com/support/downloads/File.aspx?d=2236&langtype=1031 Import this GSD in the Hardware catalogue and assigne the device to the S7-300 controller. The cognex will have a special adress rangefor exchangingUser /control data with the controller. |
8/1/2014 5:54 AM | |
Posts: 4 Rating:
|
Thanks for reply, I have GSD files and also configured.but i need to test the connection and communication (example)blocks is avilable. |
8/1/2014 11:24 AM | |
Posts: 1058 Rating:
|
Hello dramsree, I have attached Cognex In-Sight & SIMATIC S7 300 PLC ProfiNET Communication Manual here, which you would also find at Cognex webpage. Chapter 5 shows how to test communication.You should find there everythin you need. If you have any questions, dont hesitate to ask. regards AttachmentOnboard ProfiNET - IS_v1_3.pdf (2209 Downloads) |
This contribution was helpful to
1 thankful Users |
8/8/2014 7:41 AM | |
Posts: 4 Rating:
|
hello eisenpferdreiter Thanks for the reply. |
4/16/2019 10:35 AM | |
Joined: 6/19/2017 Last visit: 6/12/2024 Posts: 8140 Rating:
|
New question published by WaqasAkram is split to a separate thread with the subject Profinet communication to cognex - All addresses in tag table are "false" or "16#0000" when monitoring.. Best regards |
My Forum is the place to personalize your profile, |
|
4/21/2019 6:43 PM | |
Posts: 18 Rating:
|
Hi, By default, Checker has the PROFINET protocol disabled, so you have to enable it directly from the Checker software from Cognex: 1.In the upper menu toolbar, click Checker. 2.Select Configure Checker. You can check this for more details => https://support.cognex.com/en/downloads/detail/checker/2820/1033 |