Hello Amol V You can specify Which Flag Bytes will be updated from the Master to standby bythe parameters MB_NO and MB_LEN of FB 100 of Software Redundancy. e.g. if you set MB_NO = 100 and MB_LEN = 20 then Flag bytes from MB 100 to MB 119 will be continuously updated from the Master to the Standby CPU. ( At what speed ? ... it not clear .. Speed basically depends on the total volume of data specified to be updated from the Master to Standby CPU including DBs, MBs etc ) Any other Flag bytes areNOT updated from the Master to the Slave CPU any time( Including Changeover ). Hope this helps Cheers Navnag |