Hello Brian; You can use S7 Basic Connections and communication blocks only if both CPUs are configured as DP-masters. And if each PLC has a CP 342-5 inserted in the rack and configuration. If one is master and the other one slave, you must use master-slave acyclic data exchanges. And the interface areas of the slave must be configured for this data exchange. See fig. 3 in the following FAQ (and sample program):
DP link between CPU 315-2DP (slave) and S7-400 (master) with STEP 7 V5.3
https://support.industry.siemens.com/cs/ww/en/view/6518822 If you cannot change the slave PLC's configuration, you might have a little problem... You might want to look into using OPC to read/write between the 2 CPUs in that case. Hope this helps, Daniel Chartier |