Hello, You need one Ethernet switch to connect both PLCs and PC. On PLCs side eventually you will need CPs (for example - 6GK7343-1CX10-0XE0). Eventually depends from type of CPU. And in SCADA software just you need to assign both connections one with the first PLC and the other with the second CPU. Best regards, Hristo Mihalev |