4/8/2010 9:34 AM | |
Joined: 10/7/2005 Last visit: 4/24/2024 Posts: 3004 Rating: (1046)
|
Hello ScodeS first of all I have to say "well done" for checking the Diag info and provding the info here. What the above bold tells me is thatthe I/O's configuration of theDP Slave in Step 7's HWconfig does NOT match the physical "make up" of the DP Slave (and the DP Slave as such rejects the I/Oconfiguration from the Master and will not enter data exchange). An example on how to get thiskind of message is this: You physicallyplugged together an ET200M station with one 32 channel DI module in Slot "4" and one 32 channel DQ modulein Slot "5". In Step7 HWconfig you do however configure the DI module for slot "5"and the DQ module for Slot "4"(or configure a16 channelmodule, orconfigure only one module, etc. etc.) Please check the above and make sure your Step7 configurationmatches that of the DP Slave. I hope this helps (andif it doesn'tplease post the DP Slaves GSD file here together with your Step 7 project). |
Cheers |
|
4/8/2010 12:06 PM | |
Posts: 15 Rating: (1) |
Fritz, Thanks for taking the time to help me out. Please excuse the state of my project. HW Config is OK, though. I'll attach GSD separately. Thanks Steve Attachment888-100.zip (157 Downloads) |
Last edited by: ScodeS at: 4/8/2010 12:11 PMYou''ll see from my project that I have several slaves. My project will eventually have 3 (node 11,12,13). I have previously done testing on Node 15 which is OK. I have recently been trying to connect to Node 12. |
|
4/8/2010 12:07 PM | |
Posts: 15 Rating: (1) |
GSD
AttachmentYORK095_GSD.zip (139 Downloads) |