1/5/2010 8:55 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, You have to use a GSD and not the 315 of the standard catalog. GSD can be found here: http://support.automation.siemens.com/WW/view/en/113652 Import the GSD in the HW Catalog first. Than Drag the new added slave type (somewhere under Profibsu DP) in the network. |
Best regards |
|
1/7/2010 10:40 PM | |
Joined: 7/2/2008 Last visit: 3/14/2023 Posts: 928 Rating:
|
Hello dzwilu, In addition to what jklm had already said, you can find detailed description with steps in, Configuring an S7 CPU as DP slave on the H system using a Y-Link. Best regards. H-H |