Joined: 8/10/2006 Last visit: 1/16/2025 Posts: 156 Rating: (3) |
Dear All, We have to communicate S7-400H AS with energy automation system AK 1703 on ethernet. I havent find any helpful material on below energy automation link: https://www.energy-portal.siemens.com/irj/portal/ptd/public/en/global-04/home?prodname=AK1703ACP Please help me in this regard. Thanks, Raheel |
Last edited by: CS Moderator at: 2/19/2009 11:17 AMTransferred to internet |
|
2/25/2009 11:18 AM | |
Joined: 8/10/2006 Last visit: 1/16/2025 Posts: 156 Rating: (3) |
Dear All, Finally after correspondance with Siemens Vienna we came up to the attach solution for establishing communication between S7 400HPLC with SICAM AK 1703 ACP over profibus. Since SICAM1703 is always acting as Profibus Master so we have to use Profibus DP/DP Coupler for linking two master systems.TheGSD file of DP/DP coupler can be added in simatic hardware configuration. For any further information feel free to contact me. AttachmentRTU SAT AK1703 to S7_400H Communication Configuration.pdf (280 Downloads) |