8/31/2017 12:10 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi Brian, you need to wire the network redundant too. see this manual: SIMATIC PROFINET System Description chapter 4.11 and this FAQ may help you too: Configuration Examples for S7-400H with PROFINET hope this helps, regards, |
FCK WAR! |
|
9/2/2017 2:42 PM | |
Joined: 7/2/2008 Last visit: 3/19/2025 Posts: 928 Rating:
|
Hello Brian, The answer is yes and no in the same time. For S7-412-5,414-5.,416-5 and 417-5 (configured in SIMATIC Manager), the answer is NO. What you would like to have is a system redundancy feature which exists only on Profinet IM153-4. For PCS7 V9.0 and CP 410 H, the answer is Yes by using the new Profinet Y switch (similar to Y couplers in Profibus). Best regards, H-H
|