Hello Seroj; J_Bell is right in that only Profibus and Etehernet CPs are supported for redundant connections on S7-400H systems. Refer to the S7-400H manual for more details. Manual S7-400H Fault-Tolerant systems: http://support.automation.siemens.com/WW/view/en/1186523 Basically, the solution proposed is a CP 341, setup as a Modbus RTU slave in a redundant ET 200M chassis, with a single connection to the Modbus master's bus. This way, whatever the active S7-400 CPU, the connection to modbus is maintained at all times. You would simply program the CP 341 slave as a standard Modbus RTU slave, based on the Modbus slave manual. http://support.automation.siemens.com/WW/view/en/1218007 See the foolowing links: How do you download a loadable driver such as "Modbus Master (RTU)" into a CP341 that is connected to an S7-400 H system by means of an ET 200M? http://support.automation.siemens.com/WW/view/en/17854293 Does S7 400H support redundant CP441? (Note specially Late's post) /tf/WW/en/Posts/8389 |