6/23/2013 10:44 AM | |
Posts: 3 Rating:
|
CPU I am planning to use is S7-416H, 6ES7416-5HS06-0AB0. Because it has 94 Open IE Communication resource maximum. Please advise. |
6/23/2013 2:06 PM | |
Posts: 515 Rating:
|
Hi, You can use IM 153-4HF module which supports profinet. Kindly refer the below link |
6/23/2013 2:41 PM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating:
|
Hello, Have a look at this Thread.... https://www.automation.siemens.com/tf/WW/en/Posts/62086 Hope this helps. |
Last edited by: O_Moderator at: 6/23/2013 5:44 PMLast edited by: Amit_86 at: 6/23/2013 2:43 PMVANDE MATARAM..... |
|
6/24/2013 8:21 AM | |
Joined: 9/6/2008 Last visit: 5/7/2022 Posts: 1121 Rating:
|
Hi Well S7400 Hot redundant System supports Profibus and not Profinet. But if you use the profinet in ring redundancy it is possible to use it in S7400 H system. Further more you can use the S7400- 416 via profinet. But please tell us what is the IO requirement. How many AI, AO, DI,DO modules are you planning to use. See the Load on the controller is decided by the no of AO and DO (PID / Control) it is going to use. If your system has only Digital then you can use the same. But be carefull it is advisable to break your system into little part say you can have single controller for 20 areas or so. Typical configuration |
Jazz |
|