2/2/2014 2:56 AM | |
Joined: 10/7/2005 Last visit: 4/17/2025 Posts: 3047 Rating:
|
Hello AUDIONE73 I'm afraid to say that the "common" problem is the way you use the OLM G22. Put simple, the redundant Profibus of a H-System requires two physically seperate Profibus Networks (one per CPU). Even thoughan OLM G22 has 2 RS485 ports, theseare internally linked together via repeaters and all OLM G22 portsbelong to ONE logical Network. The press release statemenet of theOLM-G22 is still correct, but note that the word "Segment" is used in it. Segments are created within a Network when a repeater is used, but itstill remainsONE Network (and you need two physically seperate Newtorks). The only solution I see for you is to buy more OLM's (G12's will do the job as you don't really seem to have a need for the second RS485 port). I hope this helps |
Cheers |
|
This contribution was helpful to
1 thankful Users |
2/3/2014 3:16 PM | |
Joined: 10/7/2005 Last visit: 4/17/2025 Posts: 3047 Rating:
|
Correct dear AUDIONE73 the only way to achieve whjat you want to do is to change your design to a dual redundant fiber optic ring which means you'll need double the amount of OLM's that you currently have foreseen. |
Cheers |
|
2/6/2014 6:04 AM | |
Posts: 3 Rating:
|
Hello Fritz, Thank you very much for your comments. Best regards BC |
This contribution was helpful to
1 thankful Users |
9/8/2014 3:06 PM | |
Joined: 11/23/2006 Last visit: 2/25/2025 Posts: 3 Rating:
|
Hi, Second group of OLM's added. Problem solved. Best regards. BC |
This contribution was helpful to
1 thankful Users |
9/24/2015 4:45 AM | |
Joined: 1/2/2014 Last visit: 4/16/2025 Posts: 150 Rating:
|
Can you share the final configuration??? |