7/12/2010 1:16 PM | |
Joined: 7/2/2008 Last visit: 3/19/2025 Posts: 928 Rating:
|
Hello acquanat, 1- The IM153-1 is no longer available. You should switch to IM153-2. 2- You should have 2 rings (One for each CPU). S7-400HCPU1---high speed fiber----S7-400H CPU2 | | |Cu |Cu | | |----OLM1------II----OLM2------| | II | |---OLM3------II----OLM4------| | | |Cu |Cu IM153-2 IM153-2
Best regards. H-H |
7/13/2010 12:01 AM | |
Joined: 7/2/2008 Last visit: 3/19/2025 Posts: 928 Rating:
|
Hello acquanat, Would you please tell me what you are trying to do in details? What kind of IM will you use? The S7-400H can have various configuration of distributed I/Os. You can read more under Chapter 10 (Using I/Os in S7-400H) in SIMATIC Fault-tolerant systems S7-400H manual. If you have one sided DP slaves (e.g. drives) you can use Y-Link and OLMs but if you are going to use IM153 then it's not a good thing to use Y-Link. For Y-Link with IM153, please check this thread. Best regards. H-H |
7/13/2010 2:11 AM | |
Posts: 6 Rating:
|
Hi, please see attached file to see part of the plant we have to setup. I'm waiting for official french siemens help but France is on Holliday till september
AttachmentVisio-S7-400H Optical Loop technical forum.pdf (177 Downloads) |