Hello!!! Any One Having Example Program For MODBUS Communication Using ET200SP With S7-400H CPU...
|
7/11/2017 4:23 PM | |
Joined: 1/3/2009 Last visit: 6/30/2022 Posts: 161 Rating:
|
I suppose you are using Modbus RTU slave with ET 200SP serial module. Attached, sample project. Everything works fine, except something I was not able to fix: in case you remove serial module from I/O rack, there is no way to re-estabilish communication, unless you STOP the H system and restart (for example, from CPU switch). Modbus registers are stored in DB100 Regards Attachment400h_modbus.zip (349 Downloads) |
Stefano Angioni |
|
This contribution was helpful to
1 thankful Users |
7/12/2017 4:04 AM | |
Joined: 7/30/2012 Last visit: 2/24/2025 Posts: 335 Rating:
|
Hello Thanks for Your Reply |