5/4/2009 8:22 AM | |
Posts: 433 Rating:
|
Hi Damon, I can't help you with this FC, I don't know it. Perhaps another user can help you... But for Profibus Diagnostics you can use Systemdiagnostics DP/PA Slaves as well. In tab "Download" you can download a demo version for testing. This addonworks for redundant systems definitely. Tomcat |
5/5/2009 10:40 AM | |
Joined: 7/2/2008 Last visit: 11/27/2023 Posts: 928 Rating:
|
Hello, Idon't think FC 125 or even FB125 would work with slaves after Y-Link on H-System. I'm curiousto know how you filled the parameter DP_MASTERSYSTEM. Which DP_MASTERSYSTEM did you use (1 or 2 or 5980)?! One more thing, FC 125 uses SFC 51. I don't know which SSL_ID is used inside but I've seensomeone hereon forum saying that SFC 51 failed to diagnose DP slaves behind Y-Link because the DP_MASTERSYSTEM_ID (5980) can't be accepted. I think it can't even work directly with the ET200M direct slaves. It's the same reason, which DP_Master are you going to diagnose in H-System (1 or 2). Try to useFC125and alter the DP_MASTERSYSTEM parameter according to which CPU is MASTER. I'm not even sure that it might work this way. I don't have enough hardware to test it now For DP slaves behind Y-Link, the manual says you can use SFC58. I'm afraid that if FC125 doesn't work, you will have to write your own code anddesign your own screens. Best regards. H-H |