6/29/2009 8:58 AM | |
Joined: 3/21/2006 Last visit: 1/13/2025 Posts: 10239 Rating: (1182) |
Hello, I guess you have Step7 v5.4 SP4. Try with installation of SP5. Regards Hristo Mihalev |
6/29/2009 10:23 AM | |
Posts: 4 Rating: (0) |
SP5 has been installe, but it didn't help. I have made a new project from scratch, but it didn't help... |
6/29/2009 10:29 AM | |
Posts: 160 Rating: (16) |
Can you upload your config for review? |
6/29/2009 10:35 AM | |
Posts: 4 Rating: (0) |
Yes, here it is.
AttachmentTest2.zip (179 Downloads) |
6/29/2009 11:33 AM | |
Posts: 160 Rating: (16) |
HI, Sorry I did not realise you were trying to configure a connection via Netpro. Unfortunately only S7-basic connections can be established via Profibus betwen S7-300 stations. Just to clarify it is possible to establsih a S7 connetcion only when you are using a CP and relevant FB's. Please refer to the techincal data of the CPU's for this information to see if it supports client and /or server roles. Please refer to the following link for information with regards to communications in Simatis capabilities. http://support.automation.siemens.com/WW/view/en/20982954 Please refer to the folowing link for a guide to establshing Client / Server Communication with (I) Slaves via S7 Basic Communication (I_PUT/ I_GET) http://support.automation.siemens.com/WW/view/en/20987910 Maybe this would be of better use for you. |
Last edited by: mumbles at: 6/29/2009 11:42 AM |
|
This contribution was helpful to1 thankful Users |
6/29/2009 11:59 AM | |
Posts: 4 Rating: (0) |
Thankyou, this was excatly what i needed. |
6/29/2009 12:06 PM | |
Posts: 160 Rating: (16) |
Glad to help and happy programming |