Dear all, Recently I found out that Step 7 V5.6 HF 4 and HF 5 unable to insert a 4-subconnections S7 fault tolerant connection. Only V5.6 HF 3 can do so. HF4 and 5 can only insert a 2-subconnectiotn S7 fault tolerant connection. CPU a R0- CPU b R0 CPU a R1-CPU b R1. R0 - R1 or R1 to R0 , connection will be down. |