4/22/2009 9:10 AM | |
Joined: 10/9/2007 Last visit: 5/14/2024 Posts: 1241 Rating: (115) |
Hi As gateway you could you Sicam PAS. It is a PC-based solution with a software dedicated to substation and energy automation. It is certified by Kema and isa product from Energy Automation division from Siemens. In comparison to a driver in S7, you have the advantage of reading fault-records directly from protection devices, capacity to connected 150 devices in one system or upto 350 in distributed system (1 server and additional computers as interface processors) and up to 20.000 datapoints to be read from these devices. Depending on the hardware you are using, you simply import the ICD/SCD file into Sicam PAS and just choose which information you want from a table. If the number of equipments and data volumeis low, you can use a driver inside S7-300/400 or PCS7. More informations about this product, as limits and necessary work to import variables you find here: http://www.industry.siemens.com/industrial-services/it/en/PRODUCTS/SIMATIC_ADD_ONS/S7_IEC61850.HTM Mike J |
Energy Automation products: Sicam, Siprotec, Digsi |
|
This contribution was helpful to3 thankful Users |
5/14/2009 12:26 PM | |
Posts: 3 Rating: (1) |
Take a look http://www.siemens.com/s7_iec61850 |
6/19/2009 2:22 PM | |
Posts: 3 Rating: (1) |
Mike is right. Update speed is limited. Reporting is scheduled for a futureversion. |
3/8/2013 1:59 PM | |
Posts: 1 Rating: (0) |
You can use wago 750-872 with IEC61850 integrated. I test it and it's work fine. |