11/1/2010 8:36 AM | |
Joined: 10/7/2005 Last visit: 9/11/2024 Posts: 3020 Rating: (1054)
|
Hello annupalani If you do not write to the DQ's anymore in your program, they will remain in their laststate. Can you check in Variable Table (VAT) if the DQ's are 1? If so, you can now also reset them to 0 in the VAT. If the DQ's are all 0 in the VAT, I suspect an issue eitherthe DQ card and/or with the wiring. I hope this helps and pelase let us know the outcome. |
Cheers |
|
11/1/2010 7:18 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating: (11) |
Palani, What is the type of DO card? Regards, Behnam www.sigmaprocess.ca |
11/2/2010 12:48 PM | |
Posts: 26 Rating: (2) |
Hi Behnam Plz. note the card model: 6ES7322 1BL00 0AA0 Thanks BR Palani S |
11/2/2010 1:22 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating: (11) |
Palani, I have attached the Block Diagram of Digital Output Card. If the output is not energized, the only way to have LED on is that the Zener Diode for that channel is not working properly which let 24VDC directly on the resistor. Have you replaced the cardwith a spare one? Regards, Behnam www.sigmaprocess.ca AttachmentS7-300 DO Card.pdf (158 Downloads) |