12/27/2007 8:04 PM | |
Joined: 1/7/2006 Last visit: 3/9/2025 Posts: 2705 Rating:
|
Hi, How many of this slaves do you have on the network ? It seems that something is bringing down the power, are there too many resistors on the network, do this particular slave have the possibility to do the terminationby his own. If the versamax slave is on the end of a segment then check if the slave is giving a good termination, see the connections in the attached zip-file. Try it first with one of those slave(s) and check all the connections..... On which Master are those slave(s), please consider that you may have 31 slaves behind one master (for Profibus the RS485 devices are counting). When you have more then use a repeater RS 485 Repeater up to 12 MBaud - [6ES7972-0AA01-0XA0] please! If non of the above helps then please place the hardware (export cfg-file from Hardware configuring) here on the forum. Please also place the GSD file on the forum so that I could look carefully what is happening. AttachmentConnections Profibus.zip (566 Downloads) |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|