7/23/2021 3:58 AM | |
Posts: 25 Rating: (1) |
Find the solution, thanks all. Share with all of you below. (2) SINAMICS G120X Speed Control via SIMATIC in TIA Portal - YouTube |
Last edited by: Jen_Moderator at: 07/23/2021 08:45:00Embedded video. |
|
This contribution was helpful to1 thankful Users |
7/23/2021 9:06 AM | |
Joined: 4/28/2015 Last visit: 10/22/2024 Posts: 1278 Rating: (301) |
Hi, easiest way is to use the SINA_SPEED FB in your PLC program. With this one you can enable the drive and give your speed setpoint via standard telegram 1. What the FB does automatically is to normalize the speed setpoint. I guess this is what you are asking for. The speed is not simply transferred as a real rpm value - it is a normalized value, depending on the speed reference in the drive (p2000). That's why you have to set up the speed reference value to the FB. From this value and your wanted speed setpoint the FB will calculate the correct value that needs to be send to the drive. Find an application example for G120X with speed control here: |
Last edited by: RB91 at: 07/23/2021 09:08:15Best regards, |
|
This contribution was helpful to1 thankful Users |
7/26/2021 5:44 AM | |
Posts: 25 Rating: (1) |
Yes, I have download the library, it works with TIA PORTAL. Drive_Lib_V62_S7_1200_1500 |
This contribution was helpful to1 thankful Users |