I have experienced the same things as well. If you can update your PLC firmware to the latest (I think that is 3.0.2), or confirm it is already there, you can submit a Support Requestfor any work-around. The work-around I found was to switch those tags causing problems to absolute addressing in the HMI and it suddenly works. Of course, power cycling works, but is less convenient. From what I have gathered,it is a plc glitch, not an hmi glitch. |