2/12/2007 8:09 AM | |
Posts: 7 Rating:
|
Hi Thanks for replay but I want to communicate with PC'sethernet card to CPU(315-2DP) I must not CP card Thanks for helps |
2/12/2007 9:39 AM | |
Joined: 4/24/2006 Last visit: 3/14/2025 Posts: 8894 Rating:
|
Hi, When you want to use the PC's ethernet card, you will need a CP-card in S7 PLC. You need a CP343-1 Lean. And software Softnet S7 Leanfor industrial ethernet. Here is a link how to make the connection work: http://support.automation.siemens.com/WW/view/en/22333149 I hope this will help. Best regards, Wizard |