Hello KhanhLe, Process data from master is transferred to the slave (IM153-2) in the same network while data from standby CPU is discarded in assigned redundant slave.In case of switch-over, last valid data are locked by the redundant DP slave assigned by master and when the switch-over finishes, process data from new master is transferred to outputs.Read more in "4.1 How does a system with software redundancy work?' of the following manual: http://support.automation.siemens.com/WW/view/en/1137637 I hope this helps, Hamid Hosseini |