11/14/2010 2:20 AM | |
Joined: 9/27/2006 Last visit: 4/30/2024 Posts: 12257 Rating: (2666)
|
Hello SpaceBee; You do not use a Wizard in Step 7 (for S7-3-- and S7-400 CPUs), you must use the integrated functions FB41, FB42 or FB43. For a DC motor control, which would be a continuous control, I would suggest you study FB41. Also, you do not use the transfer function directly in the Step 7 program. You must use the techniques provided at school to deduce from the transfer function of the process (not simply the motor) the required values for Proportional gain, Integral time and Derivative time (the PID parameters) that optimize your controls. If you would like another guide for this calculation, look at the controlguru.com webpage, where you will find many interesting discussions on the subject. Look especially at Section 2: PID controller design and tuning. In the meantime, here are a few links to application notes and FAQs that will help you setup the FB41 function block properly: Description of PID control FB41 (see also the online help of Step 7): http://support.automation.siemens.com/WW/view/en/589983 What should you watch out for when calling and assigning parameters to the controller functions in function blocks (S)FB41, (S)FB42 and (S)FB43? Where can you find descriptions and examples of PID control with FB 41, FB 42 and FB 43, and SFB 41, SFB 42 and SFB 43? Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 11/14/2010 2:20 AM |
|