6/1/2010 1:13 PM | |
Posts: 103 Rating: (6) |
Hi, AttachmentProposed Configuration_R2.pdf (294 Downloads) |
6/1/2010 4:32 PM | |
Joined: 2/6/2009 Last visit: 1/7/2025 Posts: 939 Rating: (118) |
DearPPND,
Yes it is possible to switch over the CPU's with the communication cable failure signal from the WinCC. In R-system, it is possible to switch over the R-system CPU’s by ‘SWR’ standard block input. For Ex: Set a bit in (Status Bit) one of the CPU (CPU1) and Reset the same bit in other CPU (CPU2). If the CPU1 communication cable breaks and in the WinCC you will “Status Bit” as 0. Set another bit from WinCC (“Switch over Bit”), if the “Status Bit = 0” and use the same in the PLC logic to switch over from CPU1 to CPU2. |
_______________________________________________________________ |
|