Hello, SIMOTION doesn't support the safety telegram 30 by it's own. To work with this telegram you must use a Simatic F-CPU to communicate with the SINAMICS trough SIMOTION. The SIMOTION work as a safety proxy between the safety plc and the drive. For more Information refer the Safety Capter in the communication manual of SIMOTION http://support.automation.siemens.com/WW/view/en/61055999Capter 8 Regards Christoph |
5/21/2013 10:53 AM | |
Joined: 10/11/2006 Last visit: 4/17/2025 Posts: 6008 Rating:
|
Hello, Another document is this standard application example: http://support.automation.siemens.com/WW/view/de/50207350 It contains a description for the communication configuration. It contains also a small overview in chapter 4.9 about the displaying of safety functions in simotion. Another document is containing more informations about the axis technolgy object of a simotion itself: |