5/12/2011 1:32 PM | |
Joined: 9/23/2005 Last visit: 4/29/2024 Posts: 4325 Rating: (1426)
|
Hi, Note: the v13 SP1 / V14 versions of this project were publish in a post, here, at 27/sep/2017 AttachmentData Logging.zip (16134 Downloads) |
Last edited by: Pegaia at: 9/12/2011 12:26 PMAbout the sw version for the sample program Last edited by: Denilson Pegaia at: 9/27/2017 9:47:27 PMDenilson Pegaia |
|
This contribution was helpful to62 thankful Users
|
7/1/2011 3:33 PM | |
Posts: 4 Rating: (2) |
Thank you. Can Iask a question? -Where can change the file name of the datalog? (banana) . |
This contribution was helpful to1 thankful Users |
8/2/2011 1:00 PM | |
Joined: 8/21/2010 Last visit: 5/2/2024 Posts: 6 Rating: (1) |
Hello! How can I transfer the Logged data into 24 MB MMC? |
9/2/2011 10:23 PM | |
Joined: 9/23/2005 Last visit: 4/29/2024 Posts: 4325 Rating: (1426)
|
Do you have SP1 or SP1 update1? |
Denilson Pegaia |
|
9/12/2011 2:41 PM | |
Posts: 7 Rating: (0) |
hi, i have STEP7 10.5 SP1 regards |
9/13/2011 12:49 PM | |
Posts: 25 Rating: (0) |
Impossible to open ? it's a zip-file, did you extractit ?? I was able to open it. My question ; I tried theexample on my home-PC & PLC and from the 1st try, I was ableto view the data log files. When I added the example to myreal program (other PC and PLC), I usedother markers and markerwords, but I suppose it's working because I see the nr Created increase when I do a DataLogCreate and the same when I do a DatLogWrite.So I suppose the logging is working. When I go to theinternet explorer, I get a datacommunication error instead of that screen of the S7-1200 CPU Webserver. My IP-addresses are 9.0.0.1 for the PC and 9.0.0.10 for the PLC and I enter http://9.0.0.10/ in my internet explorer. What is the problem here ??? If I close the file with a DataLogClose, it doesn't help. Is it necessary that the siemans-software is open and the a certain screen is activated or other preconditions ? Has it something to do with the IP-address starting with 9 instead of 10. Is it because it's another type of ethernet-port??? bart I found the answer (stupid) : enable the webserver in the properties of the configuration of the PLC |
Last edited by: BSALV at: 9/13/2011 3:04 PM |
|
1/16/2012 10:17 PM | |
Posts: 20 Rating: (1) |
I don't understand what i should do it. Can you explain more precisely. I'm doing everything it what was wrote in first post Pegaia |
1/19/2012 9:51 PM | |
Posts: 20 Rating: (1) |
Hello I'm attaching the watch table and a warnings what i have when I'm compile software. I'm doing everything the same what You are writing in first post. |
2/9/2012 11:51 AM | |
Posts: 23 Rating: (0) |
Hi, I have S7 1200 1212C with 2.12 firmware but I can`t use data logging. I don`t have SP1. Could that be the problem?
|
2/9/2012 2:29 PM | |
Posts: 23 Rating: (0) |
Thank you! I`m downloading the third part and I`ll try it when it`s done.
|
2/13/2012 7:51 AM | |
Joined: 8/31/2010 Last visit: 5/15/2024 Posts: 1509 Rating: (222) |
Hello HristoAtanasov , You can alternatively try to access the *.csv files using the S7-1200's integrated Web Server. Working with data logs in S7-1200so that you can confirm atleast if the data log is created. The complete details on DATA LOG instructions of S7-1200, Working with DATA LOG in S7-1200 is available here - DATA LOG in S7-1200 - Data Logging in S7-1200 |
Like it? Rate it! |
|
This contribution was helpful to1 thankful Users |
2/13/2012 10:53 AM | |
Joined: 9/23/2005 Last visit: 4/29/2024 Posts: 4325 Rating: (1426)
|
Hi Polonez, Here there is a cast about my DATA LOG operation. I suggest you recompile HW and SW (all) before download it. I suggest you also reset to the factoring sets before the download. Attachmentoperating.zip (1962 Downloads) |
Denilson Pegaia |
|
This contribution was helpful to1 thankful Users |
2/14/2012 4:35 AM | |
Joined: 8/31/2010 Last visit: 5/15/2024 Posts: 1509 Rating: (222) |
Hello HristoAtanasov, * Refer here to know on "How to set time of day using PG/PC?" * Here you find the instructions related to the Real Time Clock in S7-1200 - Date and time of day instructions |
Like it? Rate it! |
|
2/24/2012 11:25 AM | |
Posts: 6 Rating: (2) |
Hi Guys, is there a way to tell how full a datalog is? in other words I want to know before the log is full that it needs to be uploaded. |
2/25/2012 1:56 PM | |
Joined: 8/31/2010 Last visit: 5/15/2024 Posts: 1509 Rating: (222) |
Hello ok69a, Check here on Limits to the size of data log files in S7-1200 Make sure you don't exceed this in your application |
Like it? Rate it! |
|
4/16/2012 12:41 PM | |
Joined: 9/23/2005 Last visit: 4/29/2024 Posts: 4325 Rating: (1426)
|
Hi, what is the command sequence that you are doing? |
Denilson Pegaia |
|
10/18/2012 4:32 PM | |
Posts: 1 Rating: (0) |
hi Pegaia |
1/18/2013 10:37 AM | |
Joined: 9/23/2005 Last visit: 4/29/2024 Posts: 4325 Rating: (1426)
|
Hi Once you have already create a datalog (anyway), you should not give the command to create it again (make no sense). It should be worked by user software: either save the information that you have alread created the log, or manage the errors codes of the blocks. The blocks "Data Log Open"; "Data Log Close"; "Data Log New File" are descripted in the S7-1200 System Manual (36932465 ) chapter 8.7. Here a quck description, copied from that: Data Log Open Opens a pre-existing data log file. A data log must be opened before you can write new records to the log. Data Log Close Closes an open data log file. DataLogWrite operations to a closed data log result in an error. No write operations are allowed to this data log until another DataLogOpen operation is performed. Data Log New File: Allows your program to create a new data log file based upon an existing data log file. |
Denilson Pegaia |
|
This contribution was helpful to1 thankful Users |
1/23/2013 4:24 AM | |
Joined: 8/31/2010 Last visit: 5/15/2024 Posts: 1509 Rating: (222) |
Hello All, Find one more exhaustive application example which is released recently and it discusses on Process Data Acquisition and Monitoring with SIMATIC S7-1200 (Data Logging)with the new possibilities which enhances the usability of Data Logging in S7-1200. |
Like it? Rate it! |
|
1/30/2013 12:23 PM | |
Posts: 11 Rating: (0) |
Hi Pegaia Thanks for the response, is there information about pulses in any of the manuals which i can follow to sort this data logging out? Irvin |
2/3/2013 10:50 PM | |
Posts: 11 Rating: (0) |
I couldnt find the table you specified in the system manual-is ot possible you made an error? |
2/4/2013 2:12 PM | |
Joined: 7/7/2010 Last visit: 5/14/2024 Posts: 14724 Rating: (2364)
|
https://support.automation.siemens.com/WW/llisapi.dll?query=s71200+system+manual+04%2F2012&func=cslib.cssearch&content=adsearch%2Fadsearch.aspx%3Ftab%3D2&lang=en&siteid=csius&objaction=cssearch&searchinprim=_searchinprim_&nodeid=99&x=16&y=8&cssearchengine=NEW&x=0&y=0 That link brings up the current system manual. The table numbers change between revisions. It is rev date 04/2012. |
science guy |
|
3/21/2013 1:45 PM | |
Posts: 6 Rating: (0) |
Is it possible to send the CSV file to e-mail using the instructions TM_MAIL? |
6/10/2013 10:30 AM | |
Posts: 25 Rating: (0) |
is there a way to save the data log on the memory card without the web server ? and how ? thank you
|
6/10/2013 11:23 AM | |
Posts: 11 Rating: (0) |
I am sure you can view the datalog on the memory card if you removed it and put into pc, but using the webserver you can access it much easier without interrupting your system by removing memory card. |
6/11/2013 1:12 PM | |
Posts: 25 Rating: (0) |
i checked the memory card and the data logs were saved there too. as you said, its much more easier to use the web server than to use the memory card. Thanks alot.
|
7/18/2013 6:58 PM | |
Joined: 6/26/2013 Last visit: 9/5/2022 Posts: 2 Rating: (0) |
HI: IS necessary yo have a siemens Memory card or can I use any memory card? second: how can I see and send data using my own page user on my S7-1212C? thank you. |
7/20/2013 7:08 PM | |
Posts: 27 Rating: (0) |
I am working with a 1214C CPU with a 24 MB memory card. I have made an datalogging program based on your example Pegaia. I have the following problem. My datalog starts to overwrite the values at 25 records. Which is strange. No matter what value I write at the records input of the datalogcreate block. I log the following variables: Cycle numbe: string[11] Description: string[30] Measurement: [string] The csv file is 9kb large when I transfer and look at it, so the format that I am loging can't be too large, can it? Any input would be helpfull. Thanks in advanced. Best regards Ales
|
7/22/2013 9:19 AM | |
Posts: 11 Rating: (0) |
Are you opening the file by just clicking the name in the webserver or are you actually downloading the file and saving it first? I have noticed that it shows only 25 when you just click on the name. Click on the download (floppy symbol), save it then open it and you should see everything. |
7/23/2013 10:49 AM | |
Posts: 27 Rating: (0) |
Hello IrvinC. Yes this was the reason, I was clicking on the link not on the floppy diskette. I was curious and inserted the SD card in to my computer and saw that all the data logs are 1 MB large. So I opened them and all the records were complete. So then I inserted the SD card back to the PLC and tried to download it by clicking on the diskette and it downloaded the complete file. Strange that the link has a sort of preview function, this should be stated somewhere IMHO. Thanks Best regards. A |
7/23/2013 11:01 AM | |
Posts: 11 Rating: (0) |
You can change the number of entries to view (just below the link) to what you require and then see more records that way if you wish. |
12/31/2013 5:56 PM | |
Posts: 62 Rating: (0) |
Hi all. I've got a question regarding of the read out of the real variable in a data log. Is it possible that the real variable would be written in this format to the datalog: 55.5 not like this5.500000E+01.
Doubt it, but it's worth to ask. Thanks in advanced, and have a great 2014 every one!!!! Cheers |
12/31/2013 7:34 PM | |
Posts: 20 Rating: (0) |
Hello, If you get those data in an EXCEL file, you will be able to transform the value format by selecting the boxes and chosing "number" instead of "scientific". These are the French terms that I translated in English, I don't know if it corresponds to the English terms. I hope it can help you. Anyway, I wish you a happy new year. |
This contribution was helpful to1 thankful Users |
1/2/2014 5:48 PM | |
Posts: 62 Rating: (0) |
Thank you for the info, I'll convert it like so. Cheers
|
1/21/2014 2:54 PM | |
Posts: 340 Rating: (6) |
new question is splittet to using data logging blocks in 1200 plc. |
3/8/2014 8:35 AM | |
Posts: 1 Rating: (0) |
dear sir con we use memory card for this and how to define path and interval for data loging. |
3/10/2014 10:50 AM | |
Joined: 9/23/2005 Last visit: 4/29/2024 Posts: 4325 Rating: (1426)
|
Hi, the past interval is defined by user program, by the requisitioncommand of the write block. E.g. high precision time intervals could be get with time interval OB's. |
Denilson Pegaia |
|
5/22/2014 4:15 PM | |
Posts: 67 Rating: (1) |
thanks you |
12/11/2014 12:00 PM | |
Posts: 25 Rating: (0) |
Hi, I have additional requirements. 1) In this program if data reached to record number limit it stops recording, How to overright data, and get latest last 100 records. 2) How to clear the memory, and under same name start recording from beigning. Thanks in advance
|
1/9/2015 9:58 AM | |
Posts: 25 Rating: (0) |
Hi O_Moderator, No answer to my last post. In addition to that: 1) How to delete last created files. 2) Every time if I make changes like increase number of variable, change type of variable, it stops recording than I have to change the name of file every time. 3) It is not recording variables more than 3. How to increase number of variable for recording. Thanks in advance! |
1/22/2015 10:21 AM | |
Joined: 9/23/2005 Last visit: 4/29/2024 Posts: 4325 Rating: (1426)
|
Hi, up to now, the only way to delete a data log is from Web interface. It not possible to match in a same data log two or more different data structures. |
Denilson Pegaia |
|
This contribution was helpful to1 thankful Users |
1/27/2015 5:25 PM | |
Joined: 3/11/2007 Last visit: 4/14/2024 Posts: 226 Rating: (13) |
Good evening, I have some concerns on the use of the datalog. I do not understand why you do not create the headers of the columns, and because the data is not displayed in the column as it is represented in the system manual. You may aiutamrni. I enclose picture. Thank You ----------------------------------------------------------------------------------------- Buonasera, ho delle perplessità sull'utilizzo del datalog. Non comprendo il perchè non vengono create le intestazioni alle colonne, ed il perchè i dati non sono visualizzati in colonna come invece viene rappresentato nel manuale di sistema. Potreste aiutamrni. Allego immagine. Grazie |
4/8/2015 12:36 PM | |
Joined: 6/10/2014 Last visit: 10/3/2023 Posts: 10 Rating: (0) |
Hi Ganes, do you know what's the direct link for the log files for the 1500 CPU, because I've tried that in the chapter 4.2.4 and it doesnt' work, and those I've found in other threads don't work either. Thanks in advance. |
4/20/2015 4:11 PM | |
Posts: 1 Rating: (0) |
Hi, I am very new in SPS Programming World. Thank you, the attached program works fine. How fast is it possible to log the Analog signals using S7-1200(s7-1214DC/DC/DC). Is it possible to log in every 20 milisecond (may be more less). I need to log as more as data in short time for some experiments. In the given program, i have used a pulse signal, it gives the trigger to write data. If i give the pulse at higher frequency, it cannot write properly. May be because of those BUSY flags? The cycling time of my program is less than 5 ms. Regards, Milan
|
5/4/2015 4:58 PM | |
Posts: 57 Rating: (8) |
Hi. I'm trying to understand how datalogging works. I used yr sample program, and it works fine. I successfully created the datalog and wrote one record. Then I went to the web interface, found the datalago, downloaded it, and there were my data, one single record. But now.... tell me if I understand correctly: 1 - The only way to get the logged data is via web interface. My purpose would be to log data and then send them via modem to the central equipment, when it calls. The PLC software should be able to access the logged data, but how? I didn't find any way to programmatically read logged data. 2 - After reading previous posts, I think to understand that there is no way to delete old datalog files from PLC program. But if I always use the same datalog, will it work in a FIFO way, creating a circular buffer? in that case there would be no need for data delete, because they would be automatically deleted. 3 - How do address (select) the SD memory card OR the internal PLC memory for the datalogging operation? And, (matter for a different topic?) is there any other way to store data and get them later by PLC program? I can't use retentive data because of the small size of the retentive area. How to programmatically write/read/delete data on the SD card? Any chance? Thanks a lot. |
Last edited by: salrandazzo at: 5/4/2015 5:04:47 PMLast edited by: salrandazzo at: 5/4/2015 5:07:36 PM |
|
10/27/2015 8:35 AM | |
Joined: 5/18/2015 Last visit: 11/9/2020 Posts: 67 Rating: (2) |
Hi! I've succesfully managed to implement data logging in my s7-1200 PLC. My last issue is with timestamp. All I can do with datalog blocks is to set Timestamp 0 or 1. Now my logs have UTC time logged, but I'd like them to have PLC local time. PLC's time is OK. UTC+1 timezone is set correctly. While browsing through PLC's web site I can see that file is modified at 6:00 am local time, but log shows 5:00am, UTC time. Please see file attached. How can I make datalog to use PLC's local time? I could 'cheat' and set up the time zone UTC on my correct time, but UTC has no DST, while in my timezone we have UTC+1 (winter) and UTC+2 (summer) and it will be crutial. |
11/15/2015 9:58 PM | |
Joined: 1/23/2013 Last visit: 8/10/2022 Posts: 226 Rating: (5) |
Hi how to implement the file names in the form 11/11/2015.csv 11/12/2015.csv .............??? |
11/16/2015 7:47 AM | |
Joined: 4/28/2015 Last visit: 2/7/2024 Posts: 10533 Rating: (819) |
Hello, probably impossible due not correct chars -> / |
With best regards... |
|
12/19/2015 7:16 PM | |
Joined: 1/23/2013 Last visit: 8/10/2022 Posts: 226 Rating: (5) |
Hi 1. how to get rid of the time format "nanosecond" 2. Why do I get symbols ".........." |
Last edited by: SAR-CNT at: 12/21/2015 8:11:59 PM |
|
1/29/2016 12:57 PM | |
Posts: 1 Rating: (0) |
Hi, I have error: " 8092 Source data log does not exist"., when i wont to create DataLogNewFile. What is this error? Thanks! |
2/3/2016 12:33 PM | |
Joined: 12/15/2009 Last visit: 5/10/2024 Posts: 5 Rating: (1) |
hello I have one question for about DATA LOG: S7-1200 data log write record values in separate columns Please answer my question. Thanks Christopher |
2/21/2016 4:29 PM | |
Joined: 7/2/2014 Last visit: 4/25/2024 Posts: 1 Rating: (0) |
Hi... I am using your Datalog example and I need close the archive... I noticed that when the archive is closed there is a // END included at the end...It worked for some time but suddently It doesn´t close it anymore...Which is the correct function that does it? I really need to have this // END to understand that the file is finished..and then process it. I am using Tia Portal V12 SP1 Mauro |
3/2/2016 1:29 PM | |
Posts: 25 Rating: (0) |
Hi Guys, Last year i used this program and it was working fine with 1200 V11. But now CPU has changed by Siemens to 214-1AG40-0XB0 earlier it was 214-1AG30-0XB0. Now new CPU can be programmed with V13 or higher. Problem- I can see only two contents HOME and INFORMATION on web server when I access PLC on internet Explorer. any idea i can only relate it with new Hardware and Firmware. Thanks In Advance. |
3/2/2016 1:35 PM | |
Posts: 5225 Rating: (1187)
|
The FW4 hardware has some new parameters relating to the web server. |
3/8/2016 10:18 PM | |
Posts: 1 Rating: (0) |
Hi, Problem is, I tried to implement a pulse trigger and it doesn't seem to work. I used the pulse CTRL_PWM. Any suggestion on what I should use and how to use it? The TP function also generates a pulse, but it needs to be "reseted" after every pulse. Thank you in advance. |
3/10/2016 6:27 AM | |
Posts: 2 Rating: (0) |
|
Last edited by: SST1991 at: 3/10/2016 6:28:37 AM |
|
3/13/2016 8:14 PM | |
Joined: 1/17/2007 Last visit: 10/6/2020 Posts: 289 Rating: (3) |
You could count the clock bit M0.5 for 5 times if you want 5 second interval; or other combinations. What is the application?
|
4/6/2016 1:01 PM |
|
Joined: 9/30/2015 Last visit: 9/7/2022 Posts: 23 Rating: (0) |
asda |
4/14/2016 8:55 AM | |
Posts: 5 Rating: (0) |
You can read in the local time of your plc: RD_LOC_T This gives you a DTL. Use the SECONDS from this DTL Than you can use this second to create your pulse IF (#DTL.seconds mod 5=0 THEN #Pulse:=TRUE; ELSE #pulse:=false; END_IF; |
4/19/2016 3:24 PM |
|
Posts: 198 Rating: (36) |
|
4/20/2016 8:12 PM |
|
Posts: 198 Rating: (36) |
https://support.industry.siemens.com/tf/ww/en/posts/tips-and-samples-programs-for-user-defined-web-pages-and-s7-1200/61760/?page=0&pageSize=10#top https://support.industry.siemens.com/tf/ww/en/posts/tips-and-samples-programs-for-user-defined-web-pages-and-s7-1200/61760/?page=0&pageSize=10#top |
5/9/2016 2:46 PM | |
Posts: 14 Rating: (0) |
Hello , I downloaded your sample program for data logging and executed successfully. But, when I tried to implement the program in a new file I got failure. I couldn't even create a data logging file using the instruction "DataLogCreate". I am using CPU 1212C AC/DC/RLY , Version V4.1, TIA portal Version V13 SP1 Update5. Please see the attached picture. Advance thanks for your active responses. Gajan. |
Last edited by: Gajan.K at: 5/9/2016 11:14:47 PMLast edited by: Gajan.K at: 5/9/2016 11:49:35 PM |
|
3/16/2017 10:34 AM | |
Joined: 11/17/2015 Last visit: 5/9/2024 Posts: 57 Rating: (16) |
Hi! Here "Usage of S7-1200 Memory Card" is written: - At present, S7-1200 still cannot help the memory card realize such advanced functions as recipe and data archiving. But in this thread is discussing the exact opposite So what is the catch? |
7/12/2017 8:32 PM | |
Joined: 2/4/2016 Last visit: 3/31/2023 Posts: 1 Rating: (0) |
Can anybody help me, i'm new at siemens, and i have only v13 and v14, and i can't open the v11 sample share in the begin. Can someone share the program converted to V13 at least? thanks |
Last edited by: Jen_Moderator at: 7/13/2017 11:33:45 AMNew subject after splitting Last edited by: Jen_Moderator at: 7/20/2017 6:56:59 AM |
|
9/27/2017 9:43 PM | |
Joined: 9/23/2005 Last visit: 4/29/2024 Posts: 4325 Rating: (1426)
|
Hi, sorry for the delay Here there is the V13 version of the original program AttachmentData Logging_V13_SP1.zip (957 Downloads) |
Denilson Pegaia |
|
This contribution was helpful to2 thankful Users |
9/27/2017 9:45 PM | |
Joined: 9/23/2005 Last visit: 4/29/2024 Posts: 4325 Rating: (1426)
|
Hi here there is the v14 version of the original project AttachmentData Logging_V14.zip (1279 Downloads) |
Denilson Pegaia |
|
This contribution was helpful to2 thankful Users |
10/26/2017 8:54 AM | |
Posts: 1 Rating: (0) |
Please, help to understand one moment: I need to use non-optimized block access (for Weintek Panel connecting), but example doesn't work in this case (log creating, opening, but do not writing). In my program (with more complex data structure) PLC changes to DEFECTIVE MODE by attempting to write record. Thanks. |
Last edited by: Barhan at: 10/26/2017 8:57:41 AMLast edited by: Barhan at: 10/28/2017 3:27:22 PM |
|
4/9/2018 7:51 AM | |
Joined: 11/15/2017 Last visit: 3/21/2024 Posts: 78 Rating: (15) |
Does anyone have an idea how this application affects cycle times when logging larger amounts of data? I'm thinking about 50 variables every second, different data types, mostly 16-bit data types. Working with a 1518F-4. |
Last edited by: Sibrand at: 4/9/2018 8:00:03 AM |
|
4/9/2018 4:36 PM | |
Joined: 7/7/2010 Last visit: 5/14/2024 Posts: 14724 Rating: (2364)
|
With the top of the line S7-1500 PLC, you should not see significant cycle time changes. Heck, for s7-1200, you should probably not even notice a full 1ms cycle time change. There is not a lot going on. It is just moving data around, organizing data, and so on, and not really all that much of it.
|
science guy |
|
4/10/2018 2:51 PM | |
Joined: 11/15/2017 Last visit: 3/21/2024 Posts: 78 Rating: (15) |
Thanks for your answer! When i generate logs they always turn out bigger in size than i predicted. EDIT: Cut off most of my question because i found the answer on page 395 of the Manual.
|
Last edited by: Sibrand at: 4/10/2018 3:06:53 PMLast edited by: Sibrand at: 4/10/2018 3:09:58 PMLast edited by: Jen_Moderator at: 4/11/2018 8:30:17 AMOptimized link. |
|
This contribution was helpful to1 thankful Users |
12/17/2018 5:26 PM | |
Posts: 3 Rating: (0) |
Dear Gents, I have managed all related to logging bu now. But ... the order of records in CSV file is really dissappointting. as it overrides the newest to oldest one but does not re-order the coulmn elements. so it is almost impossible to use the csv as data base for chart making. i mean ... |
This contribution was helpful to1 thankful Users |
12/17/2018 6:02 PM | |
Joined: 2/8/2017 Last visit: 3/15/2024 Posts: 87 Rating: (17) |
reorder means to write all the stored values again to the sd card which decrease the lifetime of the card and needs as well processing time in the plc - make no sense from my point of view ;-) Best Regards |
4/9/2020 6:12 PM | |
Joined: 6/22/2019 Last visit: 4/1/2024 Posts: 2 Rating: (0) |
Hello Mr Denilson i tried your program, and i also have created my own, but i always get this format in csv Do you have any idea what is the problem ? Thank you very much |
4/9/2020 6:40 PM | |
Joined: 7/7/2010 Last visit: 5/14/2024 Posts: 14724 Rating: (2364)
|
That looks like a bad import into excel rather than opening a .csv file with Excel. Close excel. Find the .csv file you exported from the PLC in file explorer. Right-click and open with Excel.
|
science guy |
|
4/9/2020 7:07 PM | |
Joined: 6/22/2019 Last visit: 4/1/2024 Posts: 2 Rating: (0) |
I am afraid no difference... I have tried also with v13 and v15.1 but again the same bad format... |
4/9/2020 7:56 PM | |
Joined: 7/7/2010 Last visit: 5/14/2024 Posts: 14724 Rating: (2364)
|
Are you using Excel? If so, import the .csv file and tell the importer your data is comma separated. I think it defaults to tab delimiters. At this point, it's an excel problem, unless you are using a Linux / mac device to download the file and opening the thing in windows / excel. Use your favorite search engine for the importing of .csv files into excel.
|
science guy |
|
5/24/2021 5:28 PM | |
Joined: 11/2/2017 Last visit: 4/17/2024 Posts: 29 Rating: (0) |
Hi Denilson, I am interested in checking, how to make this program work in TIA Portal V15.1 U5? Do you have the same program for latest version, because i can't even open your version. Regards, Rahul |