5/6/2011 9:48 PM | |
Joined: 9/23/2005 Last visit: 6/7/2024 Posts: 4341 Rating: (1430)
|
Hi, I attached here a very simple sample program with S7-1200 and Sinamics G120 in Profinet.The ZIP file has the STEP7 V11 Project and the GSDML data. In principle, the main steps are: create a project with a S7-1200 CPU, import the GSDML, drag&drop it to the Network View, drag&drop the connection to the PLC, drag&drop the Telegram 1 to the drive,build a simple logic onOB1, compile all and download all and configure the device name on the drive. Attachmentpn.zip (9076 Downloads) |
Last edited by: Pegaia at: 5/9/2011 10:58 PMLast edited by: Pegaia at: 5/9/2011 12:32 PMcorreciton S7-200->1200 Denilson Pegaia |
|
This contribution was helpful to17 thankful Users |
5/7/2011 5:39 AM | |
Posts: 15 Rating: (3) |
Hi! It's interesting! Have you tested the program on real hardware? |
5/9/2011 8:32 PM | |
Posts: 15 Rating: (3) |
Another error in theme name... |
5/9/2011 10:58 PM | |
Joined: 9/23/2005 Last visit: 6/7/2024 Posts: 4341 Rating: (1430)
|
Sorry |
Denilson Pegaia |
|
This contribution was helpful to1 thankful Users |
1/22/2012 11:48 AM | |
Posts: 17 Rating: (0) |
Dear, I have go through ur prog. and also try with my S7-1200 CPU 1214C and CU240S PN, but it not communicating. i have attachment config. so give me some hint.. manual.. thank u... Regards BNCOE
Attachments71200_cu.zip (2008 Downloads) |
1/31/2012 12:32 PM | |
Posts: 8 Rating: (0) |
Hi I have tried your sample program in my project but I am not having any luck. I am using a s7 1200 to read the parameters of a G120 CU 240s PN F. It keeps coming up with an error message saying hardware submodule component moved or missing HW ID = 14. I have enclosed screen shots of the program for your viewing. I seem to have established communication ok but this error keeps coming up any time I try to download it to the device. Is it necessary to alter something in the drive to allow the plc to read its' parameters or should it allow access anyway. Regards, Liam Attachments7 1200 screen shots 1.pdf (2605 Downloads) |
2/5/2012 6:48 AM | |
Joined: 8/31/2010 Last visit: 6/6/2024 Posts: 1514 Rating: (223) |
Hello All, Check this Application Example which is recentlypublished in Applications and Tools --> Connecting a SINAMICS drive to an S7-1200 CPU in TIA Portal (via GSD file) But this application is with PROFIBUS DP |
Last edited by: Ganes10 at: 2/5/2012 9:45 AMmissed to mention abt PROFIBUS DP Like it? Rate it! |
|
This contribution was helpful to1 thankful Users |
2/15/2012 1:36 PM | |
Joined: 8/31/2005 Last visit: 5/21/2024 Posts: 2197 Rating: (326) |
Hello, The example Connecting a SINAMICS drive to an S7-1200 CPU in TIA Portal (via GSD file)shows and explaines both, process communication and parameter access. You should use it to see how it has to be done, it's not as a unique "standad function block". Even ituses a SINAMICS G120C, it is the same with G120 or S120, you just use a other GSD-file and other telegram types. Aslong as you define the same in STARTER as in STEP 7 V11 it will work. I did not use PROFINET, but I see no reason why it should be different. There are two important points to look for,when programmingthe S7-1200(see chapter 6.3):
With this exampe and Pegaias example,anybody should be able to get it to run. |
Last edited by: miami at: 2/15/2012 1:37 PM |
|
2/15/2012 4:01 PM | |
Joined: 7/7/2010 Last visit: 6/7/2024 Posts: 14771 Rating: (2378) |
[b]bold[/b] added by me to show a key point I did not know. What is the axis # that goes into the packet structure? What if I simply want to read the controller temperature with no axis configured? Starter can do it, so the PLC should be able to do that. I think it's parameter 37 in the S120 I'm working on (CU310-PN). I get errors about the slot or node or something like that doesn't exist. I will try the correct [b]HW_ID[/b] again and cycle through all 256 possible axis values and see if I can read the temperature. :( Here's what I've been told by Siemens support (US): Set up the packet for reading data. Use WRREC to send the read data requeat Use RDREC to actually receive the requested data. Is there a standard control structure that works well with WRREC/RDREC to help improve communications reliability? For example, both WRREC and RDREC seem to continue attempting to write and read as long as the REQ input is high even though the documentation states it sends one request for each leading edge low-to-high transition of the REQ input. {V11 SP2 FW2.2} I assume I should use the 'done' bit from the WRREC as the REQ input to the RDREC, but there are no good examples of this anywhere for S7-1200. Help appreciated. Cyclic comms was working within minutes, and that's a huge bonus. Acyclic (S7) does not work no matter how big a hammer I use. For example, I had 2 'loops' that incremented through the HW_IDs (0..255) and Axis (0..255) to run all possible combinations looking for the 'done' bit to go true and have a 'good' status and 'no error' output. Never got one, and yet, starter works, cyclic works. Odd, very odd. |
science guy |
|
2/15/2012 6:11 PM | |
Joined: 8/31/2005 Last visit: 5/21/2024 Posts: 2197 Rating: (326) |
As far as I know the CU is Axis 0.
This is correct, sounds easy but isn't, because every single bit must be correct.
Yes and No. Yes because there is a definition. No, because it's dependig on the datatype and numbers of parameters you want to transfer. Look into the SINAMICS S110 List Manual to find out the datatype of a parameter, e.g. P1120 is FloatingPoint32=REAL Here is a description how the dataset has be be.
Iagree, without now looking into the documentation now, I remember the transfer is finished, when the BUSY goes back to 0. Then you have to check DONE or ERROR.
Generally yes, but there are some details. Like you should use the BUSY and I found outyou may get a"drive not ready fault", then you should do nothing, just wait until the BUSY goes back to 0 again (now the 2nd time). You should try to use the FB20, DB100, DB101 and DB103 from the exampleto change the ramp up and down time of your first axis. Just to be shure to have a configuration that run somewhere. The only change you will have to do, is the ID connector of WRREC and RDREC. When this works, you can start to vary the program. The parameter access follows a definition of the PROFIBUS/PROFINET organisation, ist's the same with any PLC (or there is a tool inside, that does the job for you). Did you think about using BiCo in the S120 to put the required information on the cyclic part (process data)? |
Last edited by: miami at: 2/15/2012 6:35 PMinserted link to the S120 acyclic communication Last edited by: miami at: 2/15/2012 6:26 PM |
|
This contribution was helpful to1 thankful Users |
5/11/2012 9:35 AM | |
Posts: 2 Rating: (0) |
Hello guys, Does anyone have a success with Read/Write Sinamics' parameters via Profinet? I triedthis, butI can't make it working. Best regards |
5/23/2013 6:08 PM | |
Posts: 2 Rating: (0) |
Does anyone have a sample code or instructions for S7-1200 and Sinamics G120 with TIA v12 and Startdrive? |
5/24/2013 10:05 AM | |
Joined: 8/31/2010 Last visit: 6/6/2024 Posts: 1514 Rating: (223) |
Hello esbipa, You can have a look at the below URLs, which doesn't match your requirement 1:1 but this can help a little. SINAMICS G: Connecting of a G120 (Startdrive) using S7-300/400 (TIA-Portal) with PROFIBUS and HMI TIA Portal V12 Library with Faceplates for Controlling a SINAMICS G120 Drive with a SIMATIC S7-1200/300/400 Controller |
Like it? Rate it! |
|
7/25/2013 8:39 AM | |
Posts: 251 Rating: (11) |
can you connect s71200 with cu310? |
7/25/2013 9:54 AM | |
Joined: 8/31/2005 Last visit: 5/21/2024 Posts: 2197 Rating: (326) |
Yes, justimport the GSD or GSDML file of the CU310 in the TIA Portal and use Starter to parametrate the drive. In this FAQ you can see how to use a S120 with CU320 with the technological functions of the S7-1500. The CU310 can be used the same way. Even if you want to use control word and setpoint to control the drive (instead of the technological functions),you can find useful informations in this FAQ. |
|
|
This contribution was helpful to1 thankful Users |
9/26/2013 9:49 AM | |
Joined: 8/31/2005 Last visit: 5/21/2024 Posts: 2197 Rating: (326) |
Here it is: http://support.automation.siemens.com/WW/view/en/70155469 |
|
|
5/25/2014 8:46 PM | |
Joined: 7/20/2009 Last visit: 1/16/2024 Posts: 61 Rating: (3) |
What i need to do if i want to connect 3 sinamics G120C pn drives in the same network? |
6/5/2014 1:03 PM | |
Posts: 1 Rating: (0) |
how do you drag and drop to a plc as explained |
4/5/2015 4:32 PM | |
Posts: 1 Rating: (0) |
Thanks. It was helpful. |