12/1/2011 3:06 PM | |
Joined: 8/18/2009 Last visit: 6/17/2024 Posts: 548 Rating: (33) |
You have assigned your I/O modules to PIP1 which is updated with OB35. So, remove all networks in OB1 except network one (Report System Error). Write you program in OB35 between FB450 and FB451. Also, you don't need to call FB450 and FB451 in OB10. Best regards. H-H
|
Last edited by: RAJKIRAN at: 12/1/2011 4:19 PMThanks Rajkiran Patil |
|
12/1/2011 3:07 PM | |
Joined: 8/18/2009 Last visit: 6/17/2024 Posts: 548 Rating: (33) |
Dear H-H, From where I can change redundant I/O data block in HW configuration. |
Last edited by: RAJKIRAN at: 12/1/2011 3:08 PMRajkiran Patil |
|
12/1/2011 4:07 PM | |
Joined: 7/2/2008 Last visit: 8/26/2024 Posts: 928 Rating: (308)
|
HelloRAJKIRAN
In HW configuration> CPU properties>H parameters. Please see my attachment. Best regards. H-H |
This contribution was helpful to1 thankful Users |
12/12/2017 9:52 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (171) |
New question published by AutoGen_6932939 is split to a separate thread with the subject 412-5H PN/DP redundant could not work . Best regards |