2/9/2011 10:59 AM | |
Joined: 4/14/2010 Last visit: 2/8/2025 Posts: 525 Rating:
|
Can you explain please when we need for RS485 Repeater 6ES7972-0AA01-0XA0 how much long distance is support the profibus communication without RS485 Repeater..??? Splitted from SCADA: Basic questions. |
Last edited by: O_Moderator at: 2/9/2011 11:06 AMnew subject after splitting MS |
|
2/9/2011 11:03 AM | |
Joined: 3/21/2006 Last visit: 3/17/2025 Posts: 10239 Rating:
|
What should you watch out for when using the RS485 repeater in PROFIBUS and MPI bus systems? |
This contribution was helpful to
1 thankful Users |
2/9/2011 4:44 PM | |
Posts: 5822 Rating:
|
Hello, please check out the attached PDF, it contains the information placed in the IK PI catalouge 2007. Especially check the table on the top right side, it contains what you are looking for. Best regards J_Bell AttachmentRS485-Repeater_e.pdf (72 Downloads) |