7/16/2013 7:33 PM | |
Joined: 12/1/2009 Last visit: 2/9/2025 Posts: 672 Rating:
|
Hi Abdel-Qader, what about WinCC Telecontrol? WinCC Telecontrol can direct communicate to your relays and no PLC's will be required. Infos here: https://www.automation.siemens.com/mcms/human-machine-interface/en/visualization-software/scada/wincc-options/wincc-telecontrol/pages/default.aspx?HTTPS=REDIR It's maybe a solution for you. Best Regards. |
Give us your feedback and show us your respect! |
|
7/17/2013 7:25 AM | |
Joined: 12/1/2009 Last visit: 2/9/2025 Posts: 672 Rating:
|
Dear Abdel-Qader, In case you go for WinCC with the Telecontrol (Option package) there is no PLC required. If you prefer a PLC based solution: Yes, each PLC in the substation will act as a modbus master to the relay. And at the same time it is connected via TCP/IP to the SCADA. A central PLC is not required. Technically there are more solutions possible, therefore it would be nice to know a bit more about the system specifications/requirements. Some clients request for data storage in the PLC in case ofany communication disturbance.Then you will need to look for something else (SINAUT in example). Best Regards. |
Give us your feedback and show us your respect! |
|
7/17/2013 7:45 AM | |
Joined: 12/1/2009 Last visit: 2/9/2025 Posts: 672 Rating:
|
Dear Abdel-Qader, also kindly take a look at this brochure: https://www.automation.siemens.com/mcms/process-control-systems/SiteCollectionDocuments/efiles/pcs7/pdf/76/prdbrief/br_RTU_en.pdf Best Regards. |
Give us your feedback and show us your respect! |
|
7/17/2013 8:41 AM | |
Joined: 1/5/2013 Last visit: 11/22/2024 Posts: 283 Rating:
|
Dear TIBI68, Thank you, so this is one solution to have each substation PLC as modbus master and i think the center HMI PLC is required in order to establish GPRS connection (GPRS module) with each PLC substation but in this case i think no need to be modbus master (HMI PLC) right? just, its function to establish a GPRS connection to each substation PLC and get the external tags right? in this case, the communication protocol between center HMI PLC and each substation PLC is PROFINET or using GET/PUT in order to get the external tags. can we use another solution: each substation PLC be a modbus slave and the center HMI PLC be modbus master and the communication between them is modbus? is this solution applicable by using GPRS connections between them? Thanks |
7/17/2013 9:35 AM | |
Joined: 12/1/2009 Last visit: 2/9/2025 Posts: 672 Rating:
|
Hi Abdel-Qader, we have a small problem when you want to use Modbus RTU (possible) between the SCADA and the PLC's (RTU's = Remote Terminal Units). Your substation PLC ispermanently connected to your relay but you will only receive actualdatawhen the master PLC is connected withthe substationPLC. In between, while it is connecting to the other substation PLC'sthere is data loss. If anything importanthappened in between you will not come to know. Idon't know about your requirements. As per the documents above: With S7-1200 you can have up to 2.000 messages. With S7-300 up to 25.000 and with TIM module up to 60.000 messages. With using modbus RTU no buffering in PLC ! Best Regards. |
Give us your feedback and show us your respect! |
|