hi, At first, when you are working with USEND/URCV you have an S7-connection-communication, no Profinet-communication. With Profinet-Communication the s7-1500 would be a IO-Controller for the S7-300 as IO-Devices, like Master-Slave with Profibus. When you would do this with S7-Connection, I think it would be easier to get the communication get worked by the S7-300-CPU´s as active part of the communication and the S7-1500 as a server for the vessels. If you would like to solve with real Profinet and the S7-300 as I-Device, it should work without any blocks like USEND/URCV or IP_read or anything else. See the Profinet-manual how the I-Device works, chapter 4.8: SIMATIC PROFINET System DescriptionThe only probelm is that the IO-Controller would miss a device when it is not connected and it will show you a failure(SF-LED) and if you don´t have loaded the right OB, the CPU will go to Stop. But you can deactivate the devices with SFC12 before disconnect it from the switch. And you also mustn´t project a topology, so it is allowed to connect it in every port of the switch. hope this helps, regards, |