11/26/2019 7:31 AM | |
Joined: 4/8/2016 Last visit: 2/13/2024 Posts: 133 Rating: (45) |
Hey, 1. If you use the SCALANCE XC206-2 in the PROFINET Fieldbus, you can configure it as switch in HW Config. Just add it via drag and drop and set the name (and ip address), After configuring it and compiling CFC and the OS, you will get alarm messages if the device fails or returns. If you want to get more diagnostic information about the switch in the PCS 7 OS, for example about the status of the ports, you can use the maintenance station. 2. Yes you can also integrate SCALANCE Switches in the Plant or Terminal bus into the diagnostic screens of the PCS 7 OS (Maintenance Station). This is done via SNMP and the basic steps are: 1. Configure an OPC server in the PC station. 2. in the properties of the OPC server, in the tab "SNMP": Add the switches to the plant configuration. 3. Update the diagnostic screens 4. Compile the OS You can find more information about the steps in the maintenance station manual (chapter 5.11): https://support.industry.siemens.com/cs/ww/en/view/109767562 |
Last edited by: 51N3P at: 11/26/2019 07:31:32Kind regards |
|
This contribution was helpful to2 thankful Users |