9/18/2016 9:02 PM | |
Posts: 116 Rating: (2) |
Hello, How to program the scaling of input signal 4-20 mA to 0-1470 rpm PLC:Logo Best regards...... |
9/18/2016 9:30 PM | |
Joined: 12/18/2014 Last visit: 5/3/2024 Posts: 32953 Rating: (4073)
|
In your specific case, I would suggest a two-stage amplification. With the 1st amplifier to bring the signal (4-20mA) at 0-1000 units. With the 2nd amplifier (gain 1.47 (1000 x 1.47 = 1470)) came the sensor singal to the desired range. If you were from the start trying to reinforce the area with one amplifier to 0-1470, the amplifier block would spend a warning and it came out not exact values. Attachmentrpm.zip (276 Downloads) |
This contribution was helpful to4 thankful Users |
9/18/2016 9:32 PM | |
Posts: 5225 Rating: (1185) |
Just to make sure.... which hardware are you using? |
9/18/2016 9:47 PM | |
Posts: 116 Rating: (2) |
Hello,
Input signal 4-20mA from Inverter Best regards..... |
9/19/2016 6:54 PM | |
Posts: 116 Rating: (2) |
Hello, Sorry Iam not understand you. Can you explain in details? I want to scale 4-20mA to 0-1000 unit Gain? offset? |
9/19/2016 7:07 PM | |
Posts: 116 Rating: (2) |
Hello, How to calculate gain and offset in the analog amplifier? |
9/19/2016 7:15 PM | |
Posts: 116 Rating: (2) |
Hello,
I want to know how the analog amplifier calculate these values. |
9/19/2016 7:43 PM | |
Joined: 12/18/2014 Last visit: 5/3/2024 Posts: 32953 Rating: (4073)
|
In attachment is an excerpt from the manual of Logo 0BA8. Perhaps this is understandable. AttachmentLOGO! 8 Soft manual 0BA8 2014_06_sides_130+131.pdf (230 Downloads) |
This contribution was helpful to1 thankful Users |
9/20/2016 9:26 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4774 Rating: (123) |
New question published by andrewdaw1978 is split to a separate thread with the subject Scaling with Logo. Best regards |