1/21/2009 3:06 PM | |
Joined: 9/27/2006 Last visit: 5/30/2023 Posts: 12025 Rating:
|
Hello Stefano; How are your DP networks connected to the H-system? Standard implementation would be through Y-links, that way all slaves are connected to both CPUs at the same time, and diagnpstics will come to the active CPU. See the chapter on Y-Link commissioning for more details in the following manual: http://support.automation.siemens.com/WW/view/en/1142696 If you are connecting your DP slaves in another fashion, then you need to provide more information so we can evaluate your problem. Hope this helps, Daniel Chartier |