8/6/2021 1:15 PM | |
Joined: 6/22/2017 Last visit: 1/14/2025 Posts: 420 Rating: (57) |
Hi, have you tried this? https://support.industry.siemens.com/cs/ww/en/view/109800515 There it states, that the time of the Panel might be out of range of the certificate. Best regards |
Last edited by: ZickZackTIA at: 08/06/2021 13:16:01 |
|
8/6/2021 5:21 PM | |
Joined: 10/26/2012 Last visit: 9/2/2024 Posts: 10 Rating: (1) |
Thank you for your reminder. I've noticed that. The system time of MTP is within the validity period of the certificate. Download PLC and MTP projects, and the communication is ok. I modify the PLC certificate and download the PLC project, and MTP displays the certificate error. However, the communication of downloading MTP project again is ok. I think if you modify the certificate, MTP should only trust the new certificate without downloading the project.
|
This contribution was helpful to2 thankful Users |