2/1/2010 5:26 AM | |
Posts: 382 Rating: (47) |
Dear debasish, I agreed with Late, there is no so call a golden rule to choose the types of CPU,IO,etc. Apart from Late's input, just to add on and share with you usually how I do it:- 1] Theenvironment. e.g roomtemperature or cold environment, for temperature like -25deg,may need to consider siplus item [see this https://www.automation.siemens.com/siplus/html_76/produkte/s7300.htm] 2] The nature of the project. e.g critical process whereby you need to consider failsafe type or hot standby/redunancy system. [see this https://www.sea.siemens.com/us/Products/Automation/Programmable-Controllers/Failsafe_Redundant_PLC/Pages/Failsafe-Redundant-PLC-Distributed-Failsafe-IO.aspx?HTTPS=REDIR] and this [search for S7-400H] 3] Types of communication so as to determine the communication items [e.g OLM, ethernet switches,etc]. Communication can be fiberoptic, profibus, modbus. See these for your references:- SIMATIC NET PROFIBUS Optical Link Module OLM / P11 V4.0 OLM / P12 V4.0 OLM / G11 V4.0 OLM / G12 V4.0 OLM / G12-EEC V4.0 OLM / G11-1300 V4.0 OLM / G12-1300 V4.0 Operation manual SIMATIC S7-300/S7-400 Loadable Driver for Point-to-Point CPs: MODBUS protocol, RTU format, S7 is master SIMATIC S7-300/S7-400 Loadable Driver for Point-to-Point CPs: MODBUS Protocol, RTU format, S7 is Slave Operating Instructions (Compact) SCALANCE W786-1PRO; SCALANCE W786-2PRO; SCALANCE W786-2RR; SCALANCE W786-3PRO 4] Types of field signals to determine the types of IO cards. e.g 4-20mA, digital signals, volts, PT100, etc. SIMATIC S7-300 S7-300 Module data SIMATIC S7-400 S7-400 Automation System Module Data Hope these helps! with regards, how come |
This contribution was helpful to2 thankful Users |